    <description>&lt;P&gt;I have exactly the same issue. The thermostat has been working fine for a few years until yesterday morning.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;</description>
    <pubDate>Fri, 07 Jan 2022 20:48:22 GMT</pubDate>
    <dc:creator>Frustratingnest</dc:creator>
    <dc:date>2022-01-07T20:48:22Z</dc:date>
    <item>
      <title>Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/77194#M17244</link>
      <description>&lt;P&gt;The thermostats have been working fine till this morning. When I try to turn the thermostat up, it turns orange as expected and there is a "click" on the Heat Link. However nothing happens on the boiler. The thermostat then sits showing the room temp "18*C" and the desired temp "21*C" as if it is working away correctly. This is also shown in the app on my phone too.. The same circumstances happen when I use the app to change the temperature... Both app and thermostat update each other but do nothing to the boiler.&lt;/P&gt;&lt;P&gt;The home link when ran in manual mode, works absolutely fine. I can press the button and it fires the boiler without any issues. So at least the house is warm.&lt;/P&gt;&lt;P&gt;I have seen no error codes and have restarted both the thermostat and Heat Link to no avail. This is a wire connection btw, and the heatlink shows all three lights as green when in manual mode as well.&lt;/P&gt;&lt;P&gt;Unsure what to do here. Any help?&lt;/P&gt;</description>
      <pubDate>Thu, 06 Jan 2022 12:38:54 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/77194#M17244</guid>
      <dc:creator>bbbiby</dc:creator>
      <dc:date>2022-01-06T12:38:54Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/77370#M17301</link>
      <description>&lt;P&gt;You can hear the heat link click when the display is turned both ways, correct?&lt;/P&gt;&lt;P&gt;Would you be able to check the connections in the heat link? You only need a neon type tester or something to check the power.&lt;/P&gt;&lt;P&gt;You need to put the neon tester on terminal 1, and see if a bright light shows when NOT calling for heat, and then terminal 3 should be a dim light.&lt;/P&gt;&lt;P&gt;Then turn the display to call for heat, and then test terminal 3 should be bright light, and terminal 1 should be dim.&lt;/P&gt;&lt;P&gt;Would that be possible to check where we are to start with?&lt;/P&gt;</description>
      <pubDate>Thu, 06 Jan 2022 16:39:59 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/77370#M17301</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-06T16:39:59Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78067#M17436</link>
      <description>&lt;P&gt;Will try it out today with my electrician! I also heard that this may be caused due to faulty valves sooooo we`re gonna try all.&amp;nbsp;&lt;/P&gt;</description>
      <pubDate>Fri, 07 Jan 2022 10:20:40 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78067#M17436</guid>
      <dc:creator>bbbiby</dc:creator>
      <dc:date>2022-01-07T10:20:40Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78596#M17551</link>
      <description>&lt;P&gt;I have exactly the same issue. The thermostat has been working fine for a few years until yesterday morning.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;</description>
      <pubDate>Fri, 07 Jan 2022 20:48:22 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78596#M17551</guid>
      <dc:creator>Frustratingnest</dc:creator>
      <dc:date>2022-01-07T20:48:22Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78805#M17588</link>
      <description>&lt;P&gt;Me too have the exact same issue . Only one think which I can do from phone is the booster mode for hot water works fine. 🤦‍&lt;span class="lia-unicode-emoji" title=":male_sign:"&gt;♂️&lt;/span&gt; Tried explaining to the Google support and they send me a new heatlink but no use… still the problem continues…&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 03:20:57 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78805#M17588</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T03:20:57Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78912#M17606</link>
      <description>&lt;P&gt;&lt;a href="https://www.googlenestcommunity.com/t5/user/viewprofilepage/user-id/75693"&gt;@Josemaskil&lt;/a&gt;&amp;nbsp;and &lt;a href="https://www.googlenestcommunity.com/t5/user/viewprofilepage/user-id/75379"&gt;@Frustratingnest&lt;/a&gt;&amp;nbsp;my electrician did a few checks yday, and we re taking it baby steps. it seems that 2 eph valves MAY be not working as expected so next week the plumber will come to change. I will let you know if that was the problem or something else needs to get checked or changed.&amp;nbsp;&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 10:41:32 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78912#M17606</guid>
      <dc:creator>bbbiby</dc:creator>
      <dc:date>2022-01-08T10:41:32Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78952#M17617</link>
      <description>&lt;P&gt;I tried with a neon tester and when calling for heat through phone there are no changes.&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 12:43:04 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78952#M17617</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T12:43:04Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78963#M17620</link>
      <description>&lt;P&gt;I would suggest before trying the phone you use the display dial to call for heat.&lt;/P&gt;&lt;P&gt;There could be an issue with the connection from the phone to the thermostat! You are trying to prove the heat link is talking to the display.&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 13:21:20 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78963#M17620</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T13:21:20Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78964#M17621</link>
      <description>&lt;P&gt;The easy prove is as mentioned, check the relays. That will then prove if the Nest is working correctly.&lt;/P&gt;&lt;P&gt;You can then eliminate the Nest part before you start.&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 13:22:21 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78964#M17621</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T13:22:21Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78971#M17623</link>
      <description>&lt;P&gt;I tried and the thermostat is not communicating with the heatlink. I can hear a click sound in the heatlink when calling for heat from the thermostat.&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 13:34:44 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78971#M17623</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T13:34:44Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78986#M17626</link>
      <description>&lt;P&gt;I'm confused!&lt;/P&gt;&lt;P&gt;You say, when the display is turned to call for heat and the screen goes orange, you hear a click in the heat link - correct?&lt;/P&gt;&lt;P&gt;When the dial is turned the other way, and the screen goes to black, you hear another click - correct?&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 14:10:39 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78986#M17626</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T14:10:39Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78992#M17627</link>
      <description>&lt;P&gt;Yes&amp;nbsp;&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 14:26:32 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/78992#M17627</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T14:26:32Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79021#M17634</link>
      <description>&lt;P&gt;OK, that means the thermostat is talking to the heat link some how, the next question is - Hard wired or just wireless, or both wired/wireless?&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 15:17:12 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79021#M17634</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T15:17:12Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79026#M17636</link>
      <description>&lt;P&gt;Hardwire&amp;nbsp;&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 15:22:23 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79026#M17636</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T15:22:23Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79035#M17638</link>
      <description>&lt;P&gt;To sum up, You are hard wired, and the thermostat works fine with the display, correct?&lt;/P&gt;&lt;P&gt;You can Boost the HW from the phone, and that works fine, correct?&lt;/P&gt;&lt;P&gt;Have you tried to set the Display to the Heat Link wireless?&lt;/P&gt;&lt;P&gt;What did you find when you tested with the neon on terms 1&amp;amp;3 and 4&amp;amp;6 manually with the display?&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 15:39:06 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79035#M17638</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T15:39:06Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79047#M17642</link>
      <description>&lt;P&gt;When checked the with neon tester in manual mode terminal 1 dim light and terminal 3 bright light and terminal 4 dim and 6 bright light.&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 15:51:36 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79047#M17642</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T15:51:36Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79074#M17648</link>
      <description>&lt;P&gt;That is correct. Now when you turned the dial for calling for HEAT, and the display went to orange, what were the terms 1 &amp;amp; 3?&lt;/P&gt;&lt;P&gt;Terms 4 &amp;amp; 6, what happened to those when you called for HW - ie Boost?&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 16:20:07 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79074#M17648</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T16:20:07Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79086#M17651</link>
      <description>&lt;P&gt;&lt;SPAN&gt;1 is dim and 3 is bright and HW time 4 dim and 6 bright another thing just happened is steady green light (the power)is sort of slowly blinking&amp;nbsp;&lt;/SPAN&gt;&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 16:27:53 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79086#M17651</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T16:27:53Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79093#M17655</link>
      <description>&lt;P&gt;That means the relays are not switching. I take it you have a live feed in terms 2 &amp;amp; 5?&lt;/P&gt;&lt;P&gt;The green light at the top should be a steady green light, no blinking.&lt;/P&gt;&lt;P&gt;Can you upload a pic of the heat link connections?&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 16:37:00 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79093#M17655</guid>
      <dc:creator>Frustratedddd</dc:creator>
      <dc:date>2022-01-08T16:37:00Z</dc:date>
    </item>
    <item>
      <title>Re: Nest thermostat runs only in manual mode for heating</title>
      <link>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79098#M17657</link>
      <description>&lt;P&gt;&lt;STRONG&gt;just to let you know that the green is steady now and how can I send you a picture? The link option doesn’t allow me to do so.&lt;/STRONG&gt;&lt;/P&gt;</description>
      <pubDate>Sat, 08 Jan 2022 16:46:44 GMT</pubDate>
      <guid>https://www.googlenestcommunity.com/t5/Nest-Thermostats/Nest-thermostat-runs-only-in-manual-mode-for-heating/m-p/79098#M17657</guid>
      <dc:creator>Josemaskil</dc:creator>
      <dc:date>2022-01-08T16:46:44Z</dc:date>
    </item>