04-26-2023 03:25 PM
The compatibility checker was asking for a wire labeled C. All I see is one labeled G. Is this ok to use and where do the wires go. I have W, R, G, B, Y
04-26-2023 03:46 PM
Is the blue wire connected to the B terminal?
Your current thermostat is compatible with any of the Nest thermostats.
You might need a C wire. If the blue isn't connected to the B terminal, you can use it to create a C Wire. You'll need the Google Nest Power connector if it is connected.
04-26-2023 04:26 PM
Sadly Patrick it looks like the blue conductor was cut off and not connected.
The AC Cooling Wizard
04-26-2023 05:29 PM
If that is the case, you wouldn't need the Google Nest Power Connector and can connect it like this
Red - R to R (jumper to Rc not needed)
Green - G to G
White - W to W
Yellow - Y to Y
I strongly recommend that you install a C wire
04-26-2023 05:31 PM
I found the answers I was looking for and got it working. Thank you all for the help!
04-26-2023 05:33 PM
The blue wire was cut and not connected. I entered this into the compatability checker and found I was good to go. After working out the E294 code and sorting it out, I am living in comfort and changing the thermostat from my recliner. As God intended.