12-31-2022 06:49 AM
Answered! Go to the Recommended Answer.
12-31-2022 09:46 PM
They have W (heat) jumpered to Y (AC) which is odd.
I would only use Y and set it up as a heat pump see if it works.
B should be your C (on Trane they call it B).
Red to RC
Then match up the rest the same as the old T stat.
12-31-2022 06:53 AM
Which position should these wires go on the nest!
12-31-2022 09:46 PM
They have W (heat) jumpered to Y (AC) which is odd.
I would only use Y and set it up as a heat pump see if it works.
B should be your C (on Trane they call it B).
Red to RC
Then match up the rest the same as the old T stat.
01-01-2023 10:11 AM
Thank you