09-16-2022 10:00 AM
if yes, is there a wiring diagram?
09-19-2022 06:28 PM
Yes but the nest likes to see the power come from Rc and C (the air handler transformer).
If you connect power to Rh also coming from the boiler transformer it will confuse the nest and it wont work.
So there is a workaround that requires a relay be installed with the 24v AC coil connected to the Rh and W from the nest. Then the wires on the boiler R and W go to the normally open contacts of the relay.
When Nest asks for heat the coil energizes with 24v and the contacts close hence connecting R and W on the boiler which turns it on.
If you search youtube for relay on nest ,you will find some videos about it.