10-10-2023 03:40 PM
My original thermostat has a Y2 wire, but no Y1: see attached.
Nest app said to plug into the Y1 terminal, and the "technical info" etc finds all the wires, reports cooling + heat + stg2 heat as expected, and heat + fan work fine. But cooling doesn't work, it just seems to blow fan-air or possibly warm air.
Running the troubleshooting and in the cooling area it goes to E89, which doesn't have docs 😞
To be sure, I put the old thermostat back up and cooling works fine. Nest doesn't report any other errors; it seems to be getting power fine and otherwise behaves.
Answered! Go to the Recommended Answer.
10-28-2023 07:40 PM
i figured it out; the system is a heat pump and the wire was actually an O. I traced back to the source and hooked it up correctly, all is well.
10-10-2023 09:06 PM
@austindavid , the Y1 and Y2 are the Compressor Stage 1 and Stage 2 cooling. The E89 error is reported when there is a wire attached to Y2 and no wire is detected in Y1. You cannot have Stage 2 without a Stage 1 wire. Please post a picture of your Nest Thermostat backplate so I can see the wires that are attached. Thank you.
AC Cooling Wizard
10-28-2023 07:40 PM
i figured it out; the system is a heat pump and the wire was actually an O. I traced back to the source and hooked it up correctly, all is well.