01-27-2026 09:56 AM
I have an oil furnace heat only with 4 zones - 1 for hot water and three for heat. I have 3 theromstats that i replaced with Google Nest. They each have Red and White wires only. Low Power. SO i bought 3 google C wire power connectors. My furnace has a ARM842 that all my thermostat wires go into. I bought a AC 24 volt transformer C wire adapter (AC 24 Volt 0.5Amps) and connected it to one of the google power adapters and it worked. I then connected it to all 3 power connectors and it doesnt work. I suspect maybe it is not enough power ? i connected it exacly like the photo in your post and in the google booklet. only difference is i connected all 3 C wires from the goolge adapter together with one of the power cables from the transformer with a wire nut and then did the same with all of the reds - 3 red zone wires, each with its own wago with a wire to the google adapter and a pigtail to the transformer power wire. so 3 reds together with the wire on a wire nut. Is my transformer under powered ? if i get a different one will all be ok? any other way to do this ? again my furnace has NO comm or C connection.
Argo ARM842
01-27-2026 02:36 PM
Which Nest thermostat do you have?
Is this your valve controller?
For multiple Nest thermostats it's best to use a 24 Vac 40VA transformer. A 0.5A might work, but not reliabely.
01-28-2026 07:55 AM
@Patrick_Caezza hi thank you for the response. I have a nest learning and 2 Nest Thermostats (white with mirror face). I ordered a 24Vac transformer with 40VA so when that comes this weekend I will swap it out. Hopefully that works. Your photo is not the exact same as mine. I do not have the two connections on the top right corner and the two left boxes are inline on mine 6 across not staggered like in your photo. The labelling however appears to be the same.
I dont know how to post a photo. My valve controller is the ARM842, voltage 120V 60HZ, 20VA, relay switching action DPST,Thermostat current 0.83, single phase motor rating each circuit/control 120V AC = 1/3HP, 240V AC=1/2 HP
01-28-2026 08:22 PM - edited 01-28-2026 08:28 PM
You can post a picture like this.
Sorry about posting the wrong image. I did a search for it, and that's what came up. This looks to be the correct one, yes?
03-14-2026 06:34 AM
Jumping in the discussion as I have the same situation with 5 nest and 5 power connectors, and the same board (actually 2 of them)
I wanted to know if this wiring configuration is correct (removing the jumpers in the power connectors)
(sorry but i'm not allowed to upload images)
thank you