First, you can not put two wires into one terminal.
The jumper between the Rc and Rh terminals is not needed. Connect the red wire to the Rc terminal. The Nest will automatically jump the two together.
The white and black wires need to be separated. Take a look at the furnace and see what they are connected to.
11-20-2025 10:34 AM
thanks for the quick reply. thats how they connected it when the gen 2 was installed and seem to work fine for years. I will try to figure out what the 2 wire are. could that be why the app is showing no voltage to Rc? I'm out of town and will try the change this weekend.