I had a W1 wire error code. Constantly calling for heat. I figured it was a bad wire from the thermostat to the furnace. Replaced all the wire between the mounting plate and the furnace.
When I connect the backing plate to the wire the W1 wire is immediately energized to 24v.
Tried using jumpers from the R post on the furnace and the W1 post and I get voltage. The circuit is always closed when R is energized. This is just the backing plate, thermostat not connected.
I'm guessing the backing circuit board is toast. There should be no voltage on W1 without the thermostat connected.