I have replaced the old Honeywell TH3210D with Nest v3. I suspect I'm wired it incorrectly because the heat pump does not produce heat.
On the old thermostat blue wire connected to the Y terminal. As I read in the Honeywell manual, Y is a compressor (cooling), so I connected it to the Y1 terminal on Nest.
Then, I connected the orange wire from the O terminal of Honeywell to the "OB" terminal on Nest, as I understand that it is a heat signaling cable. But I'm quite unsure now.
Could you please point out my mistake please? 🙂
Attaching the old and new wiring as well as the Honeywell's specs.
Nest
Old Honeywell
02-17-2023 07:38 PM
Try this wiring,
Black - E to * (set as emergency heat)
White - AUX to W2 (set as aux heat)
Blue - Y to Y1
Green - G to G
Orange - O to OB
Red - R to Rc
White/Black to C
02-18-2023 07:16 AM - edited 02-18-2023 07:16 AM
Sure, I added C wire, but unfortunately, it does not work...
02-18-2023 08:58 PM
Post a picture of the terminal block on the control board in the furnace/air handler.
02-27-2023 08:29 AM
Hello there,
I wanted to ensure that everything was covered here.
Thanks for lending a hand, @Patrick_Caezza.
@bushev, I'm checking in to see if you were able to take a picture of your system's control board. This will help us move forward with how your thermostat is labeled.
Regards,
Mark
03-02-2023 09:21 AM
Hi there,
Chiming in — I wanted to follow up and see if you still need help. Please let me know if you are still having any concerns or questions from here, as I would be happy to take a closer look and assist you further.
Best,
Jenelyn
03-04-2023 07:37 AM
Hello bushev,
It has been a few days since your last reply, and we're going to lock the thread within 24 hours. If you have any questions, please feel free to create a new post.
Regards,
Mark