02-22-2023 08:49 AM
I keep not receiving notifications when my post gets commented on and the post locks, so I have updated my settings. Hopefully now I'll receive any responses.
The compatibility checker said to post my current layout. Is this compatible? If so, I am not sure where to put the orange and brown wires on the Google Nest Smart Programmable Thermostat. I have 7 wires but the nest only has 6 ports.
The last post had a commenter @CoolingWizard ask if I have a Gas Furnace and I do not. I do have heat pump with auxiliary/emergency heat. I also have two zones on my one heat pump.
02-22-2023 11:34 AM - edited 02-22-2023 11:39 AM
Hello Dcastro7,
what is the label under the White Wire on your old thermostat?
At this time I see the following:
R - Red Wire is Power In
C - Blue Wire is Power Common
G - Green Wire is Blower Fan
Y - Yellow Wire is Compressor Control
O - Orange Wire is Reversing Valve Control
AUX - Brown Wire is Auxiliary Heat
?E? - White Wire is this Emergency heat?
Unused, Black Wire
There is not normally Auxiliary heat and Emergency heat in the same system.
In a Heat Pump type system, when the heat pump is in heating mode, the outdoor coil will tend to build up frost and ice. This will need the heat pump to activate the defrost cycle. When that happens, the heat pump outdoor controller will activate the auxiliary heat. Usually this is electric heat strips inside the indoor unit. When there is a thermostat with both Emergency and Auxiliary heat, the two conductors are typically wired together in the air handler. This would allow the homeowner to activate the auxiliary heat as Emergency heat in a time when the outdoors unit failed. By doing this it provides some heat until the HVAC service company can arrive and repair the outdoor unit. The only Nest thermostat that can be set up the same way is the Nest Learning Thermostat ie., the 3rd Generation.
The AC Cooling Wizard
02-22-2023 12:16 PM
Thank you for your quick response! Yes, the white wire is labeled "E". So my wiring will only work with the Learning thermostat. Good to know!
02-22-2023 02:16 PM
If you can check the indoor unit, electrical connection area and see how the wires are terminated there, if you find out the white wire, and the brown wire are both connected to the same terminal, you won’t need the emergency heating white wire with the current Nest thermostat you have.
The AC Cooling Wizard
02-27-2023 10:22 AM
Hi there,
Chiming in — I hope you got the answer you're looking for provided by CoolingWizard. If you have further questions or concerns, please let me know as I'll be willing to assist you further.
I appreciate your help @CoolingWizard,
Best,
Jenelyn
02-27-2023 10:23 AM
Good idea--I'll check. If that's the case, would I just wrap the white wire and not connect it at all?
02-27-2023 11:14 AM
Hey Dcastro7,
You got it right. Please let us know how it goes. You can also visit this link for additional information.
Best,
Jenelyn
03-02-2023 11:16 AM
Hi Dcastro7,
I wanted to follow up and see if you still need help. Please let me know if you are still having any concerns or questions from here, as I would be happy to take a closer look and assist you further.
Best,
Jenelyn
03-03-2023 01:14 PM
Hello Dcastro7,
It has been a few days since your last reply, and we're going to lock the thread within 24 hours. If you have any questions, please feel free to create a new post.
Regards,
Mark