Nest Learning Thermostat doesn't always shut off fan when set temp is reached

johnpeet
Community Member

Installed a couple of weeks ago.  Everything seemed to be working fine, but last few days been noticing that fan stays on (or compressor shuts off) at end of cooling cycle (set temp reached).  Fan stays on for 10-15 minutes, humidity increases from 46 to 56, and, then, compressor turns on again.  Next cooling cycle, both, fan and compressor, turn off.

While this is happening, Nest displays it is cooling, and history shows as if it was cooling the whole 45-60 minutes.

No Airwave symbol (disabled it to test).

Also, while compressor is off and fan on, temp never goes above set temp, but humidity does.

Doesn't happen all the time, but a few instances during the day.

Any ideas...

6 REPLIES 6

Princesss
Community Specialist
Community Specialist

Hi Johnpeet,

 

Thanks for visiting the Community.

 

We apreciate all the details you've shared. A few things we'd like to ask-- can you tell us what type of thermostat are you using? Also, when did the issue start to happen? Lastly, can you tell us if you have tried any troubleshooting steps after you notice it?

 

We'd like to get more details regarding this so we can start some troubleshooting steps that might resolve this.

 

Best,

Princess

Princesss
Community Specialist
Community Specialist

Hi there,

 

We just want to check if you have seen our response posted above. Let us know if you have additional questions, otherwise we'll be locking the thread.
 

Best,

Princess

johnpeet
Community Member

Nest Learning Thermostat v.3. Tried disabling settings/sensors, resetting unit, resetting to original factory settings.  Nothing.  Bought a new Nest Learning Thermostat v.3, but issue remained.  Nest displays no error message. Power seemed on the low end of range at 3.67v and Lin at 20 mA, so connected a C-wire to both AC unit and Nest.  Power readings went up to 3.94v and 200 mA, and system seemed to be working fine.  No more issues with fan staying on after temp. reached.  However, that lasted for a couple of days, and, today, it happened again.

Jake
Community Specialist
Community Specialist

Hey johnpeet,

 

Sorry for the late reply. I wanted to follow up with you, and see if I could be of any help. If the fan on the HVAC equipment is running when the Nest thermostat is removed from the base, there is a chance it could be an HVAC problem. If that is the case, I would recommend contacting a pro for further help to ensure the system is working properly. 

 

Best regards,

Jake

Jhonleanmel
Community Specialist
Community Specialist

Hey folks, 

Thanks again for helping here, @Jake
@johnpeet, I hope you've got the answer you're looking for. If you're still in need of any assistance, feel free to let us know. 

Best,
Mel

Hey everyone,

We haven't heard from you in a while so we'll be locking this thread if there is no update within 24 hours. If you have any new issues, updates or just a discussion topic, feel free to start a new thread in the Community.

Best, 
Mel