I’m attempting to upgrade a regular Nest Thermostat to a 3rd generation learning thermostat. It’s a steam boiler system with the wires. W, Rh, and C. It works fine with with the regular nest. The learning thermostat can’t decide if there is no power to Rh or no power to C. Power is confirmed. Wires set and reset multiple times. I have reinstalled the regular nest and it’s working.
I have reset and rebooted. And sometimes it doesn’t like Rh and sometimes it doesn’t like C.
Suggestions?
02-18-2023 10:00 AM
It’s worth also noting the app thinks I have a forced air heat and when I go into settings/ equipment on the thermostat, there’s no way to change it to the correct heat source.
03-13-2023 03:11 PM
Hi Betsy3,
Thanks for reaching out — I'm sorry for the delay. Your Nest Learning Thermostat might be receiving an overflowing power. Could you please try to disconnect your C wire to your thermostat and see if the issue persists? Sometimes power wire is enough to provide sufficient power to your thermostat.
Best,
Jenelyn
03-16-2023 03:59 PM
Hi there,
I wanted to follow up if you still need help. Please let me know if you’re still having any concerns or questions from here, as I would be happy to take a closer look and assist you further.
Thanks,
Jenelyn
03-16-2023 05:05 PM
I ended up swapping the W and R wires from where they were in the basic nest and it worked and continues to work. Thank you!
03-16-2023 05:13 PM
Hey Betsy3,
Cool! I'm glad to hear that your issue is now resolved. Please let us know if you still have any questions or concerns, as I'll be willing to assist you further. Otherwise, I'll be locking this thread after 24 hours.