05-22-2022 05:43 PM - edited 05-22-2022 05:44 PM
Hi!
I am trying to get some compatibility information relating to a current Nest Thermostat E I have.
Setup:
AC unit (single zone) in attic, Baseboard water fed boiler (3 zone, 3 totally separate thermostats) in basement.
I have a second floor thermostat I would like to replace with Nest E. This thermostat controls the on/off for AC and the 2nd floor zone for heat.
Wiring:
RH, W (these come from one system) & RC, Y, G (there is another white color wire, not connected to anything) - There is no jumper between the RH and RC or anywhere.
How can I wire up the Nest Thermostat E?
05-23-2022 04:44 PM
The thermostat that controls the AC and 2nd-floor zone needs to be a Nest Learning Thermostat, 3rd Gen. This is because you have two separate systems and each has its own transformer.
The heat side would connect to the W and Rh terminals and the cooling side to the Rc, G, and Y terminals.