Replacing thermostat with Google Nest on Natural Gas and Heat Pump HVAC system

TexasNester
Community Member

My HVAC unit has Natural Gas and a Heat Pump.    The existing thermostat appears to be incorrectly installed because I do not have a setting that allows the heat pump to run: both "Emergency Heat" and "Heat" burn natural gas.  I have the existing wires:

C, O, E (with jumper to W2), R, G, Y

https://www.amazon.com/photos/shared/uZYPNuwhR7eimb-uah0yjQ.HdaRZd7sSNexoItwMI2uNA

 

If I tell the Nest system that I have 

C, O, E, R, G, Y

It tells me to connect the following wires but I am not sure how I will get natural gas heat with this:

https://www.amazon.com/photos/shared/3NcNi271Rc-4Wmy_45Czyw.q16ccu1g1ZxL0klXE-uIuh

 

https://www.amazon.com/photos/shared/vSDQSedtQqWvs9vWXTpCmw.Kj1PxfqawOK7mBHpYKe8w_

 

Thanks in advance for your input!

 

 

1 Recommended Answer

Patrick_Caezza
Platinum Product Expert
Platinum Product Expert

Your current system doesn't have a separate emergency heat function, and they are connecting the emergency heat switch to the Aux heat, which allows you to turn only the Aux heat on manually.

You can use any Nest thermostat.

Try this wiring

Blue - C to C

Orange - O to OB or */OB

White - W2 to W2 or W (set as Aux heat)(Jumper to E not needed)

Red - R to Rc or R

Green - G to G

Yellow - Y to Y1 or Y

The "or" is for the Google Nest Thermostat wiring

 

 


To ensure that I see your reply, please tag me using @Patrick_Caezza

View Recommended Answer in original post

5 REPLIES 5

Patrick_Caezza
Platinum Product Expert
Platinum Product Expert

Your current system doesn't have a separate emergency heat function, and they are connecting the emergency heat switch to the Aux heat, which allows you to turn only the Aux heat on manually.

You can use any Nest thermostat.

Try this wiring

Blue - C to C

Orange - O to OB or */OB

White - W2 to W2 or W (set as Aux heat)(Jumper to E not needed)

Red - R to Rc or R

Green - G to G

Yellow - Y to Y1 or Y

The "or" is for the Google Nest Thermostat wiring

 

 


To ensure that I see your reply, please tag me using @Patrick_Caezza

Hello folks,

 

I wanted to ensure that everything was covered here.

 

Thanks for the help here, @Patrick_Caezza.

 

@TexasNester, I hope you've got the answer you're looking for in terms of your system's compatibility with the Nest Thermostat. You can follow his wiring guide as your reference before installing. Also, please let us know if you need more help.

 

Regards,

Mark

His recommendation worked!

 

Thanks

Jenelyn_O
Community Specialist
Community Specialist

Hi there,

 

I'm glad that the issue is now fixed. Please let me know if you have any other questions or concerns, as I'll be willing to assist you further. Otherwise, I'll be locking this thread after 24 hours.

 

I appreciate your help, @Patrick_Caezza, and Mark. 

 

Best,

Jenelyn

This worked for me Patrick!

 

Thanks for the help!