Hi, I currently have a white Rodgers thermostat with a white wire in W, red wire in RH (with a jumper wire to RC), a blue wire in B, nothing in C, a green wire in G, brown wire in O, and a yellow wire in Y. I’m having trouble determining where the blue and brown wires should go in the nest. Any help would be greatly appreciated. A photo of the current system’s wiring is included below.
10-16-2021 02:11 PM
11-18-2021 11:12 AM
Hey TravisC,
Sorry for the late reply. I wanted to follow up and ensure you are good to go. Please let me know if you are still having any trouble from here, as I would be happy to take a closer look and assist you further.
Best regards,
Jake
11-18-2021 11:23 AM
Hi Jake, thanks for checking. I ended up hiring somebody to install it. The issue was that one of the wires (I believe it was the brown wire) was wired to the thermostat but not needed in the furnace system. The previous owners had just kept it wired to the thermostat when they updated the furnace. The blue wire was installed on the nest as the common wire (C), yellow wire - y1 - cool, green wire - g - fan, white wire - w1 - heat, and red wire - rh - power. The nest system has been working great with this wiring setup.
11-29-2021 12:43 PM
Hey TravisC,
Glad to hear you were able to get everything worked out, and the device is up and running. A little odd that they didn't remove the wire when they updated the system the first time. Oh well, everything is up and running and that's what counts. With that being the case, I am going to lock the thread. Please feel free to create a new post at any time, if you run into any questions from here.