I am having three zones EPH heating ... zone 1 is for for water boiler ( system boiler) ..zone 2 is for ground floor radiators and zone 3 is for first floor radiators ...The old control panel was having three zones options
now I have installed google 3rd generation 2 thermostats in order to control my 2 heating zones and the hot water (system boiler- also treated as a separate zone)...
so one heatlink is mapped to zone 2 heating and hot water and anather one is mapped to zone 1 heating....
Now the thermostat which is mapped with only zone 1 heating is showing the water icon ( system boiler + heat with on/off+ hot water with on/off) but water boiler is not getting turned on and the thermostat which is mapped to zone 2 heating and hot water is not having hot water icon and showing ( system boiler heat + with on/off) ... My two heating ones are working fine with the two thermostats...How I can resolve this issue?
12-11-2023 12:26 AM
Thank you for all the information provided @rony40000 . I would be happy to try and assist you with this.
From your description it sounds like the thermostats were set up incorrectly. No worries, that's an easy fix.
All you need to do is go on each thermostat to Settings> Equipment> Pro setup. There you'll select system boiler or other, for the one that controls only the heating, and on the hot water control page you'll make sure it's set to "Not connected". For the one that should control the hot water you'll also select system boiler or other but on the hot water control page set it to "On/Off". Once done, you should be good to go.