07-06-2024 01:36 PM
Just had a new boiler and nest thermostat installed. The heating side of things seems to work fine but the hot water is working in reverse. When the app and thermostat is set to heat the water the boiler is off and vice versa.
07-07-2024 04:14 AM
Do you have a Heat Link in your system? Are you in the UK?
07-07-2024 04:25 AM
Yes to both.
07-07-2024 06:52 AM
They have wired the Heat Link incorrectly, best get them back. Can you upload a picture of the Heat Link wiring, just remove the cover and take picture of the connections.
I would also ask why they didn’t explain the system correctly before leaving! That would have shown the fault.
07-07-2024 07:35 AM
07-07-2024 08:27 AM
That’s an appalling install.
Just to confirm, do you have connections in 4-5-6?
By the way , whoever installed that needs to start again!
The most important connection is just hanging there, The EARTH wire, why isn’t that connected??? Look at the connection next to T1, that’s the Earth connection, but nothing in it!
Why is the cord grip missing???
Why is the cord grip that is fitted not tightened on the cable???
07-07-2024 08:41 AM
There are connections in 4,5,6. I'll get the installer back to sort it out. Thanks for your help.
07-07-2024 08:55 AM
That’s why the system isn’t working correctly!
Connections 4-5-6 are for water, but the relays are wired in reverse, and are contradicting themselves. The attached drawing clearly shows the connections, and these are inside the thermostat box. You will see 4 is normally closed and 6 is normally open., not both!
I’m not impressed when people get so called installers doing jobs like that, the installer should be ashamed of themselves. You are the person paying for that job, at least they could leave it safe, even if it doesn’t work correctly. Ask the questions I pointed out, I would love to know their answers!
i