Is that a one wire or 2 wire humidifier? Standalone or built-in?
12-07-2021 02:49 PM
the humidifier is an Aprilaire 700 m attached to the cold air return. One wire is attached to the * terminal on the thermostat and the other to the “c” terminal on the furnace
12-07-2021 02:55 PM
Have your properly configured * wire as a humidifier in the Nest equipment setting menu?
12-07-2021 03:52 PM
Yes, or I believe so, when I test the humidifier it turns on heat, blower, and *
12-07-2021 04:34 PM
Please review enclosed https://ohmefficient.com/nest-thermostat-humidifier/
12-08-2021 01:11 PM
Thanks for sharing, I have read that before. Under the section "powered flow through humidifier there is an update for powered flow through humidifier with internal fan relay which is what i have. I wired it per their diagram with no additional relay required