01-23-2025 07:24 AM
Hello-
Heat pump system with emergency/aux heating strips. Model: Air Handler model PF4MNP036. Nest 3rd Gen.
Outside temp is 34 degrees and the max inside temp I can achieve is 70 degrees.
Aux/emergency heat turns on when in test but I do not know if it turns on to support the heat pump. I was assuming no as the inside temp only reaches 70.
I have tried Test in W1 and W2aux with white wire and the aux heat turns on and heats. I tried turning off NestSense and setting manual activation of aux at 51 degrees. Same result. I have tried setting temp to 10 degrees+ to try turning both on. Any ideas? Thanks!!!
Yellow wire -> Y1
Greenish -> G
Orange -> OB
Red -> RH
Brownish -> C
White -> W2aux***
I have tried Test in W1 and W2aux with white wire and the aux heat turns on and heats. I tried turning off NestSense and setting manual activation of aux at 51 degrees. Same result. I have tried setting temp to 10 degrees+ to try turning both on.
01-23-2025 10:07 AM
Update: I traced all wires to air handler and all wiring inside air handler is correct.
01-23-2025 09:42 PM
Can you post a picture of the original thermostat's wiring if you have it?
If you don't, can you post a picture of the wiring in the air handler
01-24-2025 01:16 PM
Hello Patrick - thanks for the response. This was not a replacement. The Nest was here when I moved in but never had to use aux heat before as Florida does not typically experience this cold of weather. As such I do not have a picture of the previous thermostat wiring. I did actually trace all the wires in the air handler and compared to the install manuals - all good.
I went out and bought a cheap Honeywell thermostat, plugged in the wires and now Aux heat is engaging when it is supposed to.
Nest device was the issue. Now its a paper weight I guess.
01-24-2025 01:16 PM
@Patrick_Caezza See above response. I neglected to add the @ like you requested.