05-06-2023 03:58 PM
I have had a nest thermostat for about 6 months works amazing with furnace. Went to turn on a/c today and it starts cooling ,turns on fan, never activates condenser, and after about 30 secs it shuts off and says cooling starting in 2 mins.. it then counts down and repeats.
05-06-2023 05:47 PM - edited 05-06-2023 05:48 PM
Hello @Sfisher , you need to help us a bit more to understand your cooling problem. Can you post a picture of your Nest Thermostat backplate showing the wires attached . Also the picture of the old thermostat with the wires attached.
The AC control system uses the Y/Y1 wire to activate the outdoor condenser unit. If your system is a split system, the wire attached to Y/Y1 goes to you indoor air handler, and a separate cable runs from the air handler to the outdoor unit. The Y/Y1 is cross connected to the wire going outside to the compressor contactor.
When you installed your Nest Thermostat, and performed system tests that is recommended at the end of the installation process? Did the unit operate then?
AC Cooling Wizard
05-06-2023 06:46 PM
It seemed to be working fine when installed, but it was winter!
I got the compressor to activate with the cooling cycle now, but the whole a/c is only running about 30 seconds. Then it shuts off and the thermostat displays a starting in 2:30 count down.
Then the A/c runs for about 30 seconds... and the cycle repeats
05-06-2023 06:47 PM
05-06-2023 07:29 PM
@Sfisher , the white wire on the Y terminal goes outside to the compressor. The red wire on the Common is going outside to the contactor too. So, are ready to do some testing? Go to SETTINGS > EQUIPMENT > the continue to equipment test. Then test cooling. It will stay on cooling until you end it. If the outdoor unit shuts down after 30 seconds, then you have a problem with the condensing unit. Either low pressure or high pressure cut out is happening.
AC Cooling Wizard
05-06-2023 07:37 PM
Ok, I will test it in the morning, hvac guy came today and said it was all in working order, it was a thermostat problem, he could replace it with a basic thermostat, but I really wanted to keep my smart thermostat.
05-07-2023 01:28 PM
I replaced the c wire and fixed everything.