07-24-2024 06:16 PM - edited 07-24-2024 07:09 PM
Hello,
Attached in the reply links below is my wiring diagram currently and trying to figure out how to map to a nest. Any help would be appreciated.
07-24-2024 06:21 PM - edited 07-24-2024 06:22 PM
@Neatbourbon I see nothing is attached to the message that you posted just now you need to upload a picture of the old thermostat that shows the wires that are attached so we can help you
If my answer helped to improve your understanding, please hit the Kudo or if my answer solved your problem then choose recommend this Answer.
AC Cooling Wizard
07-24-2024 06:40 PM
07-24-2024 06:41 PM
07-25-2024 08:22 AM
@Neatbourbon I am afraid you have made a mistake on you’re wiring. The white wire needs to be placed on the OB* terminal.
It appears you have a Heat Pump system installed. Your old thermostat used W to call for heat. The short white jumper between W and Y means your system uses the compressor to heat and to cool.
Move the White wire to the OB* terminal. You have a type O heat pump.
AC Cooling Wizard
07-25-2024 11:39 AM
Thank you for that! I made the change and still get an N261 code showing unconfigured and undetected wires with the C being highlighted in orange. Based on my prior diagram, I have the green wire in C
07-27-2024 06:39 AM - edited 07-27-2024 06:42 AM
@Neatbourbon you have no Power Common wire so the green wire belongs in G.
AC Cooling Wizard