VisionPRO IAQ to Nest Learning Thermostat

earthtraveler5
Community Member

I am wanting to replace a VisionPRO IAQ with a Nest Learning Thermostat.

Is this possible?

Please let me know if this can work.


Here is a list of my HVAC hardware.

 

NameCompanyModel NumberManual
Heat PumpGoodman ManufacturingGSH130481A A
FurnaceGoodman ManufacturingGMS81405DNA
ThermostatHoneywellVisionPRO IAQhttps://www.manualslib.com/download/711761/Honeywell-Visionpro-Iaq.html
Smart thermostatNest (Google)Nest Learning Thermostat, 3rd Generation
1 Recommended Answer

Earthtraveler5,

I guess it’s time now for the ugly truth, lol.
Your Goodman heat pump has a reversing valve that when not energized the system is in heating mode. To get AC cooling mode you have to energize the reversing valve on the OB terminal.  When your heat pump is in heating mode, the defrost control board temperature sensor closes at 31°F, that is sensing ice on the coil, and that initiates the defrost cycle and the defrost control board then sends a control call on the W2 wire of the outdoor defrost controller to the indoor unit to activate the auxiliary heating, in your case the gas furnace. In systems that do not have gas heat they have the indoor coil and usually 15kW to 45KkW of electric heating strips that are the auxiliary/emergency heat.
You sort of have the best of two worlds, depends if gas or electricity is less expensive per equivalent BTU of heat to heat your house. The problem is a normal thermostat does not have the intelligence to make that decision for you.  In the case of the Nest, and most smart thermostats, when it is programmed as controlling a heat pump it can only assume that there is auxiliary and or emergency heating.  Furthermore, the thermostat considers the heat pump as the primary mode of heat. As a homeowner you will only be able to get gas heating when you place your thermostat in emergency heat or auxiliary heat mode. Otherwise the heat pump will be your primary motive heat and it will only signal the gas to come on when the outdoor unit enters defrost cycle. 
The outdoor unit connection points are only C, Y, R, W2, G.  This picture below, from the installation manual, shows the Heat Pump Low Voltage Junction Box. 

AEC283D5-512B-499A-A21F-3C47ED803A61.jpeg
Now let’s talk about the humidifier, the humidifier has as you understood correctly, two wires one is common and one is control voltage. The humidifier is a self-contained unit that has a humidistat and a setting that the homeowner can place for the desired humidity level during heating periods. The most desired heating percentage is 50% typically. When the control wire is activated it signals to the humidifier to turn on and using the humidistat will measure the humidity and if it’s below the desired level it will activate the humidifier function. We only need to send one wire from the thermostat there and that will be the red wire and the white wire will be connected to the common in the furnace.  

The wires you have numbered will need some adjustment, #5 wire will not be used, the #6 (W2) from the furnace and outdoor unit will go to the W2(#5) position in the thermostat. All the other wires, as you deduced are correct. 

when you go through the Nest online configuration tool you will list the wires that on your old thermostat are as follows. Rc, C, Y1, W2, O/B, G, HUM. 

Ken, The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

View Recommended Answer in original post

30 REPLIES 30

CoolingWizard
Platinum Product Expert
Platinum Product Expert

Earthtraveler5,

You can convert from the IAQ to the Google Nest. There might be some Sensor Wires (S1/S2) being used you will not need with the Nest Learning Thermostat. You have heat pump system with a Gas fired forced air furnace. The question is which is the primary heat? The Heat Pump or the Gas Furnace?  Your gas furnace can act as the heat pump axillary/emergency heat and this is most likely your current setup.  Alternatively the system can be set up as the Heat Pump only does Air Conditioning cooling and your Gas Furnace is your heating system.  Your Heat Pump needs the O/B wire energized to switch the reversing valve to Heating mode.  

Ken, The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

earthtraveler5
Community Member

Thank you Ken.

My big question is where to connect the W3 / AUX2 wire and the humidifier wires. According to the
Here are some pics.

earthtraveler5
Community Member

Thank you Ken.

My big question is where to connect the W3 / AUX2 wire and the humidifier wires. 


According to the doc: Nest Learning Thermostat Pro Installation & Configuration Guide, they both need to go on the * on the Nest.
visionpro iaq thermostat wiring diagram.pngHoneywell VisionPRO IAQ _left.jpgHoneywell VisionPRO IAQ _right.jpg
Here are some pics.


CoolingWizard
Platinum Product Expert
Platinum Product Expert

Earthtraveler5,

we need make sure that 5 wires are in the thermostat wire going to the thermostat.  Your IAQ is using digital communications with he EIM. It is the EIM that controls the equipment.  

The EIM has W1:O/B wire goes outdoors to your heat pump Reversing Valve. The W2 wire goes to the Furnace to initiate Gas Heat which is the Auxiliary Heat.  W3 in the EIM goes to something I cannot see perhaps emergency electric heat strips? it also looks like you have a humidifier?

I feel that  is going to need a Nest Pro working for an HVAC company to rewire your equipment to remove the EIM and get more conductors to your thermostat.  Currently there are not enough conducting wires going to the thermostat location to handle the primary and secondary heat and the W3 and the humidifier

Ken, The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

earthtraveler5
Community Member

There are 8 wires in the cable going from the EIM to the thermostat.
It looks like W1 & W2 both go to the heat pump. W3 goes to the furnace.
Yes, there is a humidifier. There are wires to both Hum 1 & 2.
I did have a "Nest Pro" come out and he did say it was incompatible. But, I'm not so sure I trust him. I am looking for more information to see if it might work.

CoolingWizard
Platinum Product Expert
Platinum Product Expert

Chances are that Nest pro who showed up was not an HVAC professional technician. We can use the eight wires to go to the nest thermostat and it will control the heat pump, gas furnace, humidifier, and whatever the second stage heat was that hooked up on W3 of the EIM.

The wires it will be used by the nest learning thermostat third generation are:

Rc - Power In

C - Power Common

Y - Compressor Contactor

O/B - Heat Pump Reversing Valve (primary Heat)

W1 - Auxiliary Heat stage 1, gas furnace

W2 - Auxiliary Heat Stage 2, unknown

G - Blower Fan

* - Humidifier  

Ken, The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

earthtraveler5
Community Member

Thank you Ken.

Few more questions:

1. It looks like OB and Aux both go to the heat pump. W3 looks to go to the furnace. Attaching clearer pics of the wiring on the right of the EIM (Equipment Interface Module) as well as another pic of wiring for the EIM / HP / Furnace. Does this look / sound correct to you? Also, the green highlighted area of the annotated image of the wiring diagram for the EIM has been my biggest uncertainty. But, you're helping to clarify it for me.

2. There are two Humidity wires as shown in the yellow highlighted section. Looking at the left pic of the EIM, it looks like H1 also goes to C. So, my guess is that the red wire goes to C and the white wire goes to *. Does this sound correct?

3. I have attached annotated screenshots of both the Nest wiring diagram and the EIM wiring diagram with numbers of what I understand of which wire on the EIM goes to which terminal on the Nest. Does this look correct to you?

Please let me know.
ThanksHoneywell VisionPRO IAQ _right-2.jpgHoneywell VisionPRO IAQ_wiring.jpgVisionPro IAQ wiring_annotated-2.pngNest wiring_annotated.png

Earthtraveler5,

I guess it’s time now for the ugly truth, lol.
Your Goodman heat pump has a reversing valve that when not energized the system is in heating mode. To get AC cooling mode you have to energize the reversing valve on the OB terminal.  When your heat pump is in heating mode, the defrost control board temperature sensor closes at 31°F, that is sensing ice on the coil, and that initiates the defrost cycle and the defrost control board then sends a control call on the W2 wire of the outdoor defrost controller to the indoor unit to activate the auxiliary heating, in your case the gas furnace. In systems that do not have gas heat they have the indoor coil and usually 15kW to 45KkW of electric heating strips that are the auxiliary/emergency heat.
You sort of have the best of two worlds, depends if gas or electricity is less expensive per equivalent BTU of heat to heat your house. The problem is a normal thermostat does not have the intelligence to make that decision for you.  In the case of the Nest, and most smart thermostats, when it is programmed as controlling a heat pump it can only assume that there is auxiliary and or emergency heating.  Furthermore, the thermostat considers the heat pump as the primary mode of heat. As a homeowner you will only be able to get gas heating when you place your thermostat in emergency heat or auxiliary heat mode. Otherwise the heat pump will be your primary motive heat and it will only signal the gas to come on when the outdoor unit enters defrost cycle. 
The outdoor unit connection points are only C, Y, R, W2, G.  This picture below, from the installation manual, shows the Heat Pump Low Voltage Junction Box. 

AEC283D5-512B-499A-A21F-3C47ED803A61.jpeg
Now let’s talk about the humidifier, the humidifier has as you understood correctly, two wires one is common and one is control voltage. The humidifier is a self-contained unit that has a humidistat and a setting that the homeowner can place for the desired humidity level during heating periods. The most desired heating percentage is 50% typically. When the control wire is activated it signals to the humidifier to turn on and using the humidistat will measure the humidity and if it’s below the desired level it will activate the humidifier function. We only need to send one wire from the thermostat there and that will be the red wire and the white wire will be connected to the common in the furnace.  

The wires you have numbered will need some adjustment, #5 wire will not be used, the #6 (W2) from the furnace and outdoor unit will go to the W2(#5) position in the thermostat. All the other wires, as you deduced are correct. 

when you go through the Nest online configuration tool you will list the wires that on your old thermostat are as follows. Rc, C, Y1, W2, O/B, G, HUM. 

Ken, The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Thanks again Ken.

I have one more clarification question. So my annotated #5 (W1) terminal on the Nest is not used?

 

Instead, the two wires from the EIM, annotated #5 (W2/AUX) and #6 (W3/AUX2) are combining into the Nest at terminal #6 (W2/AUX).

Is this correct? 

earthtraveler5, the Aux 3 in your system goes somewhere I cannot see in your photos. What is marked as Aux 2 on the EIM should be W1 on the nest, the AUX 3 would be either W2 or Emergency Heat. 

Ken

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Hi Ken, 

In this photo, OB (4) is from the heat pump. 

AUX (5) is also from the heat pump. 

AUX2 (6) is from the furnace. 

 

So, 4 goes to OB. 5 goes to W1. 6 goes to W2? 

Where is emergency heat on the Nest? Is that W2 or somewhere else? 

 

Screenshot_20221105-204346.png

That is manufacturer sample set up.  On your EIM, the Green, White, and Yellow wires on the top right, are connected on the outdoor unit are they not? 

Ken

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Yes, correct. 

The yellow, green, and white wires that go to the top left go to the outdoor unit. The yellow, green, and white wires that go to the bottom left go to the furnace.

 

Honeywell VisionPRO IAQ _right-2.jpg

The green wire on EIM G, going to the furnace is the Blower Fan Motor control. The EIM Y/Y2 yellow wire controls the Compressor outside.  It also signals the furnace to turn on the blower when the compressor is turned on.  I figure the EIM White W3/AUX2 going to the furnace is connected to W on the furnace control board.

We need to remember that the EIM, is a fully programmable switch controller.  Each of those connections on the right, can be programmed for anything that is needed in a system.  With outdoor temperature sensor connect to S1/S2, the EIM can be programmed to turn off the Heat Pump and turn on the Gas Furnace when say the outside ambient air temperature drops to say 10°F.  Basically, at -4°F ambient the Heat Pump looses heating capacity.  

What we know is the Goodman Furnace only has R,C,G,Y,W connections on the Furnace control board.  The O/B is not on the Furnace control board. On the outdoor unit there are R,W2,Y, OB, and C.  If I can find the time tomorrow I will try to draw up a wiring schematic for the Nest to the Furnace, Furnace to the outdoor unit to help you see it with he EIM not in the picture.  
Ken, The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

That would be very helpful. Thank you very much for all your help. 

Here is a picture I created to kind of show you how the wires will run from unit to unit to unit I hope this helps you understand how to wire it.

879EC96F-6C3C-41B4-A9B3-F06017245803.jpeg

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

aatienza
Community Specialist
Community Specialist

Hey earthtraveler5,

 

Checking in — we hope you've got the answer you're looking for. Let us know if you have more questions in mind.
 

I appreciate the help, CoolingWizard.

 

Thanks,
Archie

I think I have to connected and working well. Much CoolingWizard!

CoolingWizard

You're awesome!! Thanks!!

I wish I could give you that Nest Pro payment. 

 

Here it is. Everything tested good. How does it look? 

The wiring is a bit of a mess but I think it's all connected correctly. 

 

PXL_20221107_224512927~2.jpg

 

PXL_20221107_214527436.jpg

Your Furnace should have a terminal strip with the R, C, Y, G, W on it.  The thermostat cable coming from the thermostat would be terminated on the those terminal screws, and the outdoor unit cable also terminating on the same terminal screws with the only exception being the O wire.  If it is working now correctly, you are good to leave it be.  Test your ability to manually activate the alternate heat.  I would like to make sure you are capable of doing that with the Nest thermostat. 
Ken, The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

The wires are not long enough to terminate them at the furnace.

 

I believe this is how to enable emergency heat or alternate heat, correct? 

 

Screenshot_20221107-204641.png

Screenshot_20221107-204345.png

The way you have that setup is neat is always Gas. Is that what you desire?

Ken

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Oh no.

That was just to show that I knew how to set it up as always gas. I changed it back right after the screenshot.

Was that what you were referring to about emergency heat? Or is that a different setting. 

The Nest is a very smart thermostat and it know as the air outside gets colder, the heat pump looses heating capacity.  As such, it allows you to set the condition upon which you want was switch to Gas Heat. As a homeowner you can make a decision as to when you would like to use the gas heat versus the heat pump. For example you can decide that anytime the outdoor temperature drops below 20°F switch to gas heat. Or you could say never use gas heat and just have it as an emergency reserve if the heat pump should ever fail during the winter. And you’ve already seen the third choice and that is always use the gas in stead of heat pump. 

Ken

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Like this, correct? When the temp falls below 25, use the alternate heat source, gas. 

 

Do you have a suggestion of the optimal temp to set it to? 

 

Screenshot_20221107-214705.png

I agree with the 25.  To really find the sweet spot, you would need to do a lot of math.  Basically, the heat pump uses as much electricity as the air conditioner in the summer.  You need to convert the energy cost for BTUs produced by the heat pump versus the BTUs products by the natural gas consumed.  If you can figure that math out, you can find the precise point when the natural gas becomes more efficient.  Knowing this the heat pump begins loosing heating BTU capacity when the ambient temperature falls to 30 to 35 degrees.  At -4 it’s basically done,  it will be defrosting cycling longer than it is producing heat.  

Another way to sort of figure this out, is to set your auxiliary heat to never be used, and on the first very cold night wait to see when the defrost cycle comes on and then note the outdoor temperature, add 20° and that be your setpoint
Ken

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.
If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

earthtraveler5
Community Member

Great, thanks for the info.

I really appreciate all of your help Ken. Let me know if there is anything I can do to return the favor.

Hi folks,

 

Thank you for sharing your knowledge, Ken. Big help!

 

@earthtraveler5, I hope you've got the answer you're looking for. If you're still in need of assistance, feel free to let us know.

 

Best regards,

Mark

Hi folks,

Chiming in to see if you still need assistance with this. Let us know if you have additional questions ― we'd love to help.

Best,
Mel

Hi everyone,

Just one quick final check in here since activity has slowed down. We'll be locking the thread in the next 24 hours, but if you still need help, I would be happy to keep it open. If there's more we can do, just let me know.

Thanks,
Mel