I have a W2 wire and my NEST thermostat doesn't have a spot left (only 6 terminals) with O/G being the only one left. I assume the furnace might be a 2 stage blower seeing that it is new. After install everything works but will the furnace work properly when called upon. Thanks!
09-03-2023 08:00 AM
Sounds like you have the Nest Thermostat (2020) model, which has a programmable */OB connector for this purpose. Here's what the wiring should look like (old to new). Does this not match what you're seeing?
Y - Y
G - G
C - C
W2 - */OB
W - W
R - R