I have a seven wire system my 1st stage and second work fine but my cooling will not. The unit seems to be blowing the cold air up and out of the condenser. I have a picture of my old thermostat wiring but can't upload it. I called an AC company and they referred me back to the forum. @CoolingWizard
12-17-2024 12:54 PM - edited 12-17-2024 12:54 PM
@Mykol ,
in order to upload a picture onto this community form. You first must go find the email verification that was sent to you by Google when you first created your account. Once you verify your email, you’ll be able to upload pictures.
AC Cooling Wizard
12-17-2024 01:00 PM - edited 12-17-2024 01:01 PM
12-17-2024 01:01 PM
There is a black wire behind the white wire in the same slot
12-17-2024 04:54 PM
Give this wiring a try
Red - R to Rc (jumper to RC not needed)
Yellow - Y to Y1
Blue - C to C
Orange - O/B to OB
Green - G to G
White AUX/E to W2 ( set as Aux heat)
You shouldn't need the black wire. You can check where it is connected by looking at the control PCB terminal Block in the furnace/air handler.
12-17-2024 06:06 PM - edited 12-17-2024 06:07 PM
Thank you I will give that a try and I appreciate your help.
12-17-2024 10:09 PM - edited 12-17-2024 10:10 PM
@Mykol , you definitely have a Heat Pump with auxiliary heat. A heat pump runs the compressor (Y1) for either heating or cooling. The OB wire is what energizes the heat pump reversing valve that changes the flow of refrigerant to change modes from heat to cool or vice versa.
Do me a favor and get me the model number of the outdoor unit so I can verify its capabilities.
AC Cooling Wizard