03-26-2023 09:49 AM
I have a house/furnace built in the 1980s. We have only red and white wires connected to thermostat. Thankfully they ran a third wire from the taco valves up to all three thermostats. Is it as easy as connecting the third wire to the c wire connect on nest and to the common port (second) on the taco valve?
03-30-2023 08:12 PM
Theoretically, you should be able to connect the C terminal of the thermostat to terminal 2 on the valve, the W terminal to terminal 1, and the R terminal to the 24Vac transformer.
Figure C shows the wiring that I am referring to.
04-01-2023 12:15 PM
Yes, that worked
04-05-2023 10:44 AM
Hi folks,
@Robertbiron, thanks for the update and I'm glad that the issue is now resolved. Please let us know if you have further questions or concerns. Otherwise, I'll be locking this thread after 24 hours.
I appreciate your help, @Patrick_Caezza and Jake.