Heatlink works only in manual mode

Icanu
Community Member

I installed the heatlink and the thermostat and the connection between them it's good (heetlink green light, thermostat shows temperature and all) but when i give the command to change the temperature up ,the thermostat says that it will heat up to that temp in x minutes , the heatlink "click"s but the boiler doesn,t start.

When i click on the button from the heatlink (manual mode) the boiler starts.

Can you help me?

19 REPLIES 19

Frustratedddd
Bronze
Bronze

What connections are you using at the Heat Link, and what type of boiler - combi/system??

Icanu
Community Member

A combi one - Baxi Eco Luna 24kW - an old one .. until now i was using a Computherm thermostat which worked fine ... in fact still works (i installed it back) i jut wired the wires to the heatlink in 2/3 ports 

That connection is correct for the Combi boiler

I assume you also linked between Live in and term 2?

Have you a neon tester or anything to test the contacts?

Can you uplaod a pic of the connections you used?

Icanu
Community Member

I have a neon tester but what puzzles me is that it works fine on the old one (Computherm) - the same wires ..

OK with the neon, put onto term 2 and just check you have power to that terminal.

Then put neon onto term 3 and that should be dead when NOT calling for heat, and then  put neon onto term 1 and that should be live.

Then, turn stat up to call for heat and you should hear a click, and the term 3 should be live, and term 1 should be dead.

Sometimes you can find the conatcts not closing, this just proves they are or not!

 

Icanu
Community Member

I'll try that ... thank you .. but why .. when pressing the button on the heatlink .. the boiler starts! Aren't the same both wires involved in that command?

Yes they are.

I always start from the beginning to prove everything is working correctly.

When you press the heat link button and it fires up is odd, if everything is wired correctly.

You are 100% sure you are using 2-3 NOT 5-6???

Upload a pic if you can of the connections

Icanu
Community Member

yep ... they're on 2-3IMG_5260.jpg

........................and the loop from Live to term 2 is where?

There are no more wires ... that's it

That could well be the reason why it's not working me thinks!

You need a loop from Live to Term 2.

loop.jpg

...hang on, where does term 2 come from, where is that connected the other end?

Term 3 where is that connected to the other end also?

Icanu
Community Member

I think this is my caseScreenshot 2022-04-23 at 15.37.36.jpg

You will need in that case to confirm that's your connection from the boiler.

You might have a low voltage dry contact connection, but you need to check further now.

Normal Combi boilers are wired as mentioned.

 

makes sense .. i'll check the contacts in the boiler .. clean them and i'll be back 🙂 thank you again

AnaM
Community Specialist
Community Specialist

Hey @Icanu,

 

I'm sorry for the delayed response, but it seems like you've got some assistance with your issue. Did you manage to resolve it?

DragosC
Community Specialist
Community Specialist

Since I haven't heard from you in a while, I'll have to close this thread. Should anything else come up, please open another thread and we'll take it from there. Have a good one and stay safe! 
 

DragosC
Community Specialist
Community Specialist

Hi there. I'm just following up on our last message. Do you still need our help? Keep us posted.