10-09-2024 10:45 AM
I have two Trane Air Handlers and Heat pumps using Braeburn 5220 thermostats.
The wires are:
L, O, Y1, Y2, O/B/V3, G with RC/RH on a jumper.
Is the Nest Learning gen 4 compatible with this setup?
Thanks in advance.
Answered! Go to the Recommended Answer.
10-09-2024 08:01 PM
@Azcanuk , you have a conventional HVAC system that is based on a heat pump. This is going to be compatible with any nest thermostat except you can only use a learning type thermostat such as a GEN 3 or GEN 4. The L wire is actually for a light To be turned on during emergency heat and you can ignore that one. The wire that is labeled oh is more than likely your common wire. You have a compressor that’s why you have Y1 and Y2. Your reversing valve for your heat pump is on the 0/B/V3. And of course your fan is the G.
AC Cooling Wizard
10-09-2024 02:01 PM
Can you post a picture of your current thermostat's wiring here?
10-09-2024 08:01 PM
@Azcanuk , you have a conventional HVAC system that is based on a heat pump. This is going to be compatible with any nest thermostat except you can only use a learning type thermostat such as a GEN 3 or GEN 4. The L wire is actually for a light To be turned on during emergency heat and you can ignore that one. The wire that is labeled oh is more than likely your common wire. You have a compressor that’s why you have Y1 and Y2. Your reversing valve for your heat pump is on the 0/B/V3. And of course your fan is the G.
AC Cooling Wizard
10-12-2024 12:35 PM
Thanks very much for the information! Now to find a color and backplate to go with it... take care.