04-21-2022 02:42 PM
I have a wire that is giving off 24 volts; however, it is NOT connected to the boiler--it's just a power source. Do I NEED it to be connected to the boiler in order for the system to read it as a C wire?
Currently I have an R wire, and W wire and I have the 24 volt wire hooked up as the C wire. But it is saying I don't have a C wire.
Readings on the power say:
Vin: 35.133v
lin:385 (W)
PS: W-385, WP-2
04-21-2022 09:16 PM
The C wire is not just 24Vac. It is the return (common) of the 24Vac for your system.
One problem with boilers is their red and white wires are mostly just used for a switch closure and there isn't any voltage on them.
Normally 24Vac is supplied by the R wire and the C wire is the return just for powering the thermostat.
04-25-2022 05:14 PM