Nest Thermostat E now Boiler go s into Lockout

jeremywar
Community Member

I have an old heat-only boiler system with two zones, each with its own pump and relay switch. Not actually a zone controller valve. I have two thermostats each with TT wires (Rh & W) from relay switches. I recently replaced both thermostats with Nest Thermostat Es. As I don’t have a C wire I installed an nest power controller/adapter at each relay switches (x2) and I also added an external 24v transformer for each power controller configuration. 

 

Now both nest are reading and working as normal, no errors and good battery charge. However now after a few good heating cycles the boiler goes into lockout mode and stops heating.

1 Recommended Answer

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@jeremywar, depending on the boiler that you have, those systems are not designed to have 24 V of power enter on the T terminal. Some do some do not. If yours does not accept that it will see their stray voltage coming in on T and it will force the system to lock out until it gets checked.

the way to wire this up in such a way is to not have this problem is the transformer has to supply power on the RC and the C terminal. The RH and the W terminal are separate and you set the system up as a dual fuel system. The boiler will be hooked up to Rh and W. 

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

View Recommended Answer in original post

1 REPLY 1

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@jeremywar, depending on the boiler that you have, those systems are not designed to have 24 V of power enter on the T terminal. Some do some do not. If yours does not accept that it will see their stray voltage coming in on T and it will force the system to lock out until it gets checked.

the way to wire this up in such a way is to not have this problem is the transformer has to supply power on the RC and the C terminal. The RH and the W terminal are separate and you set the system up as a dual fuel system. The boiler will be hooked up to Rh and W. 

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.