Hi Electrician252,
Thanks for reaching out to us. Yes, you are correct. Connecting an external 24VAC transformer to a 2-wire system on an old furnace without a common wire (C-wire) can cause issues. In a typical HVAC system, the red wire (R) supplies power from the furnace or air handler to the thermostat, while the common wire (C-wire) provides a return path. In systems without a C-wire, power is sourced only from the red wire. Introducing an additional 24VAC transformer could create a conflict and potentially damage the Nest thermostat or other HVAC system components.
You have the option to use the Nest Learning Thermostat or Nest Thermostat E instead, as these types of thermostats may operate without a C wire since they have an internal built-in battery that can supply power to the thermostat. Another option is to run a new C-wire from the furnace or air handler to the thermostat. This may involve running additional wiring or using alternative methods like power stealing or wireless adapters to create a C-wire connection.
Let us know if that helps.
Best,
Zoe