Wiring 2 wire milliamp system and 2020 Nest

Spar
Community Member

This is about controlling a gas fireplace with a millivolt gas valve and automatic fan. The pilot is always on. So all I need is on/off in response to set point.

I'm looking to replace an existing 2-wire thermostat (Acumen model K) with a new Nest. I have a 24 VAC transformer to provide charging power. From the geniuses on YouTube I've absorbed that I should attach the the transformer wires  to C and R on the mounting plate. Since we're dealing with AC, polarity is not an issue. 

Some sources indicate the thermostat (millivolt) wire should go to W and R, that is, two wires in R.

Questions 

1. Any missing or incorrect assumptions?

2. Do I need a relay to isolate the Nest?

Thanks!

2 Recommended AnswerS

johnCNA
Bronze
Bronze

The C terminal is normally wired as a common in systems.  If it were DC voltage, it would be "ground".  Or if you're versed in A/C wiring, think of R as Hot, and C as Neutral.

Thermostats are a simple switch which connects R to W when heat is called for.  W feeds 24vac to the high side of a furnace board relay, the other side of the relay is connected to C.  You would need two terminals on the gas valve; W and C.  I have no idea of what current level is being used though, nor how much current the gas valve would require.  Personally, I'd use a low-current 24v relay to switch the gas valve, just to be sure I didn't overload the Nest.  But yeah, it could work.

View Recommended Answer in original post

Patrick_Caezza
Platinum Product Expert
Platinum Product Expert

You have to install a relay to control your millivolt system.  A circuit like this will work.

 

Boiler wiring.jpg


To ensure that I see your reply, please tag me using @Patrick_Caezza

View Recommended Answer in original post

5 REPLIES 5

johnCNA
Bronze
Bronze

The C terminal is normally wired as a common in systems.  If it were DC voltage, it would be "ground".  Or if you're versed in A/C wiring, think of R as Hot, and C as Neutral.

Thermostats are a simple switch which connects R to W when heat is called for.  W feeds 24vac to the high side of a furnace board relay, the other side of the relay is connected to C.  You would need two terminals on the gas valve; W and C.  I have no idea of what current level is being used though, nor how much current the gas valve would require.  Personally, I'd use a low-current 24v relay to switch the gas valve, just to be sure I didn't overload the Nest.  But yeah, it could work.

MelbaDT
Community Specialist
Community Specialist

Hey folks,

 

Thanks for answering to this and for your suggestions, johnCNA. 

 

@Spar, I just wanted to drop by and ensure everything is covered here. Feel free to reply back if you have more questions. 

 

Best, 

Melba

 

 

Patrick_Caezza
Platinum Product Expert
Platinum Product Expert

You have to install a relay to control your millivolt system.  A circuit like this will work.

 

Boiler wiring.jpg


To ensure that I see your reply, please tag me using @Patrick_Caezza

Spar
Community Member

Thanks John and Patrick. Installed the relay today and lo and behold it works. Feeling accomplished.😉

Ryan_G
Community Specialist
Community Specialist

Hey folks,

 

Thanks for visiting the Google Nest Community. 

 

Since this thread hasn't had activity in a while, we're going to close it to keep content fresh.

If you have additional questions, feel free to submit another post and provide as many details as possible so that others can lend a hand. 

 

Hope this helps!

 

Kind regards,

Ryan