06-22-2022 03:00 PM
I have a Honeywell Chronotherm Thermostat with 4 wires coming out of the wall. It controls both the heat and air conditioning.
White going to W post
Blue going to Y post
Green going to G post
Red going first to Rc post then continuing to the Rh post
Nest instructions say I do not need a jumper but I am not sure which Post I should put the red wire to Rc or Rh
Any help would be appreciated. Jon
06-28-2022 12:38 PM
Hi JBliss,
Thanks for reaching out. You can put the red wire to either Rc or Rh and you don't need to put a jumper because the Nest Thermostat will use it's internal jumper between the Rh and Rc connectors. The Nest Learning Thermostat will automatically use this internal jumper if your system needs it.
Thanks,
Edward
07-01-2022 04:07 PM
Hey JBliss,
I wanted to follow up and see if you are still in need of any help? Please let me know if you are still having any trouble from here, as I would be happy to take a closer look and assist you further.
Thanks,
Archie
07-03-2022 09:38 AM
Hi JBliss,
Just checking in to make sure that you've seen our response. Please let us know if you have any other questions or concerns as I will be locking this in 24 hours.
Thanks,
Edward