01-13-2023 11:59 AM
I have a gas-fired, heat only, forced hot water heating system with two zones and two Nest thermostats that don't have C wires. Can I use a single Power Connector to handle both Nest thermostats, or do I need two separate Power Connectors? If one Power Connector can handle two thermostats, where can I find the right wiring diagram?
01-13-2023 01:57 PM
Each Nest needs its own power connector.
The R and W go directly to the R W on the power connector.
Then the wiring at the boiler is different depending on if you have 2 zone valves, or if you have 2 switching relays that control 2 circulators. Post pics of the wiring at the boiler to determine where you will connect the C wire at the boiler for the power connectors.
Or if you can pull new 5 conductor thermostat wire to each Nest then you don't need the power adapters.
This has all the info about the power connector.
https://support.google.com/googlenest/answer/10523126?hl=en
01-16-2023 03:01 PM
OK, thank you. This case can be closed.
01-20-2023 04:07 PM
Hy HenryJ,
That's great to hear! Let us know if you have other questions as I'll be locking the thread after 24 hours.
Thanks,
Archie