06-18-2022 12:31 AM
I have wired in the CH as instructed with a loop live from L to 2 and the switch line to 3 CH works fine.
for the hot water I have wire a loop love from 2 to 5 and the switch live NO into 6 however 6 is permanently live even when I take the switch live out terminal 6 is showing 240v is this a faulty heat link ?
06-19-2022 01:40 AM
Hi there, thank you so much for reaching out. Can you tell me what type of heating system you have? Is it a S plan or Y plan?
06-20-2022 08:48 AM
What do you have at term 4? Any power? Term 4 should be no power.
Also, is the bacteria icon showing?
06-20-2022 09:31 AM
Correct no power at T4
06-20-2022 03:18 PM
That's correct.
What is the bacteria set at, On/Off?
Try factory resetting, as I have found that works sometimes.The relay for some odd reasonn gets stuck.
Failing that, you could have afaulty Heat Link.
06-22-2022 12:04 AM
Hi there @Peterj, Thanks for letting us know. Please go into Settings > Equipment > Continue > Bacteria Prevention > Disable. Let me know how it went.
06-24-2022 12:06 AM
Hi there. I'm just following up on our last message. Do you still need our help? Keep us posted.
06-26-2022 01:07 AM
Hey there, I haven't heard from you in a while so I'll be locking this thread. If you have any new issues, updates or just a discussion topic, feel free to start a new thread in the community. Thanks, AlexD.