Is this thermostat compatible?

85A4E724-819E-4A83-91AA-C79A876EC306.jpeg

16 REPLIES 16

CoolingWizard
Platinum Product Expert
Platinum Product Expert

Based on the Wiring, it looks like you have a Heat Pump. The odd thing is the yellow wire in Y terminal has a White jumper wire to W1.  There is a green wire on G and a blue wire on O; the heat pump is the O wire. 

from the status of the way, this thermostat was wired, a call for heat would initiate a call to the compressor outdoors to turn on; This is the jumper between W one and Y.  There is a wire connected to the O terminal, which is controlling the heat pump reversing valve. In this case, if indeed, you have an O model heat pump, then you would need to energize the O wire in order to get heat. Where are my confusion comes is that this thermostat knows about heat pumps. Hence it has an O and a B terminal. There should not be a  need for the jumper between Y and W1. 

Can you provide the the make and model number of your old Thermostat? I would like to check the manual for configuration settings of that thermostat.  

The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Sure. I have two. One is a Braeburn 1020-150-03 and the other is a Bradburn Model 5000

CoolingWizard
Platinum Product Expert
Platinum Product Expert

On the back of your 1020-150-03 thermostat, what are the switch setting? This model is not a programable thermostat and it knows how to work with heat pump. On the back of the thermostat are some switches.

CONV/HP? Should be HP

HE/HG? Should be HE (unless you also have a gas furnace)


The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

CONV/HP is set to HP

HE/HG is set to HE

And the C/F switch is set to F

 

JV66
Community Member

The directions I got from Google/Nest help were the following

Please insert the Y wire of the old thermostat to the Y terminal of the Nest Thermostat.
Please insert the W wire of the old thermostat to the W terminal of the Nest Thermostat.
Please insert the G wire of the old thermostat to the G terminal of the Nest Thermostat.
Please insert the RC wire of the old thermostat to the R terminal of the Nest Thermostat.
Please insert the O wire of the old thermostat to the O/B terminal of the Nest Thermostat.

CoolingWizard
Platinum Product Expert
Platinum Product Expert

The white wire in W is a jumper wire to Y. It should be ignored. 

The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

CoolingWizard
Platinum Product Expert
Platinum Product Expert

If you decide to replace this with a Nest Thermostat or a Nest Learning Thermostat, you will ignore the white wire jumper between Y and W1.  You nest will use the following wires:

Red Wire on Nest R or Rc. This is the Power input. 
Yellow Wire on Nest Y or Y1, this is compressor control

Green Wire on Nest G. This is indoor blower fan control

 Blue Wire on Nest O/B. This is reversing valve control. 

The nest thermostat prefers to have a Power Common wire. Since the white wire is not attached, it could be re-purposed as the common.  

The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

So, don't attach the white wire coming out of the wall?

CoolingWizard
Platinum Product Expert
Platinum Product Expert

The model 5000 thermostat is a programable thermostat. It too has switches on the back for configuration. What are they set to?

HE/HG

NORM/HP

 

The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

HE/HG is set to HE

NORM/HP is a HP/NON-HP switch and it's set to HP

 

CoolingWizard
Platinum Product Expert
Platinum Product Expert

That is correct since it’s not currently connected to anything, there’s no reason to assume that it must be connected at this time. So just ignore that white jumper just like you’re ignoring the blue jumper between Rh and R. 

The AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

So the Google Home/Nest app is telling me that it's not compatible. They asked for the current wiring, said it won't work and I can't progress. See attached.IMG_7904.PNGIMG_7905.PNG

CoolingWizard
Platinum Product Expert
Platinum Product Expert

Re run the compatibility test using only R, Y, G, O.  As I stated the white jumper between Y and W1 is to be ignored. That means you do not have a wire on W1.  Second, you only input R and ignore the blue jumper wire between Rh and R. 

The AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner. If my answer solved your problem, click Recommend this Answer below, and If it helped you, please give a Kudo.

Hello there,

 

I wanted to stop by and see how I could help.

 

Thanks for lending a hand here, @CoolingWizard.

 

@JV66, It appears you have the Nest Thermostat 2020 model based on the screenshots taken during the set-up. With this, please select only these wires that you have:

 

  • W/W1
  • Y/Y1
  • G/G1
  • R
  • O/B

 

Let me know if that helps.

 

Best,

Mark

Jake
Community Specialist
Community Specialist

Hey there,

 

I wanted to check in and see if you are still in need of any help. Please let me know, as I would be happy to assist, and answer any questions you may have.

Best regards,
Jake

Jake
Community Specialist
Community Specialist

Hey there,

 

I want to ensure you are good to go, and everything is working properly. Please let me know if you are still having trouble, as I will be locking the thread in 24 hours due to inactivity.

Best regards,
Jake