In existing Honeywell ChronoTherm III T8601C (with wires R, G, B, W, Y ) . White wire is connected to O terminal , Yellow wire is connected to W terminal. Also W and Y and connected using jumpers. I want to replace this with Nest. Need help with wiring.
Update: I have Heat pump model CPE30-1AB Goodman heat pump. Very Old Model but runs geat...running for 30th year.
pl help with the wiring.
Nest terminals are as shown in pic
Answered! Go to the Recommended Answer.
06-17-2023 03:57 PM
Connected Y G R W , Blue wire to O/B
then went to Device settings Configuration in Home App ---> thermostat > Heatpump-> Highlighted Heat pump wire to O.
This worked.
06-12-2023 02:57 PM
Give this a try.
White - O to */OB
Yellow - W to Y (jumper to Y not needed)
Green - G to G
Blue - C to C
Red - R to R
06-14-2023 10:41 AM
I will try it today
06-17-2023 01:52 PM
I connected White wire to terminal O/B on Nest
Yellow wire to terminal Y on Nest
Green wire to Terminal G on nest
Blue wire to Terminal C on nest
Red wire to Terminal R on nest ....
Set up Nest for cooling ... only heat come up ..indoor temp started rising
So changed wire configuration from above to as here -- connected White wire o Terminal W on nest , Connected Blue wire to Terminal C on Nest. This too caused heat, indor temp started increasing..
Help needed
06-17-2023 01:53 PM
I connected White wire to terminal O/B on Nest
Yellow wire to terminal Y on Nest
Green wire to Terminal G on nest
Blue wire to Terminal C on nest
Red wire to Terminal R on nest ....
Set up Nest for cooling ... only heat come up ..indoor temp started rising
So changed wire configuration from above to as here -- connected White wire o Terminal W on nest , Connected Blue wire to Terminal C on Nest. This too caused heat, indor temp started increasing..
Help needed
06-17-2023 01:55 PM
connected White wire to terminal O/B on Nest
Yellow wire to terminal Y on Nest
Green wire to Terminal G on nest
Blue wire to Terminal C on nest
Red wire to Terminal R on nest ....
Set up Nest for cooling ... only heat come up ..indoor temp started rising
So changed wire configuration from above to as here -- connected White wire o Terminal W on nest , Connected Blue wire to Terminal C on Nest. This too caused heat, indor temp started increasing..
Help needed
06-17-2023 02:52 PM - edited 06-17-2023 02:53 PM
Hello there,
I wanted to stop by and see how I could help.
Thanks for looking into this, @Patrick_Caezza.
@Honeywell_sk, I see no wire connected specifically to the Y terminal from your old thermostat, only a jumper wire. With this, I'd suggest resetting your Nest Thermostat to its default setting and continuing the setup process. Please make sure to select the same configuration suggested above.
Once the setup is complete, activate your system and let us know how it goes.
Regards,
Mark
06-17-2023 03:57 PM
Connected Y G R W , Blue wire to O/B
then went to Device settings Configuration in Home App ---> thermostat > Heatpump-> Highlighted Heat pump wire to O.
This worked.
06-18-2023 07:12 AM - edited 06-18-2023 07:15 AM
@Patrick_Caezza Sorry. There was a typo in my previous answer, which has worked. Below is correct wiring which worked
then went to Device settings Configuration in Home App ---> thermostat > Heatpump-> Highlighted Heat pump wire to O.
This has worked. Can you think of any issue in this wiring?
09-07-2023 08:51 AM
Hi everyone,
I'm sorry for the delay. I know it's been a while already. Thanks for checking it with us — I'm glad that it's working. It looks like all the wires are connected to its correct terminal. Please monitor your Nest thermostat performance and efficiency. If anything comes up, let us know.
I appreciate your help, @Patrick_Caezza and Mark.
Best,
Jenelyn
06-11-2023 12:29 PM - edited 06-11-2023 09:53 PM
In existing Honeywell ChronoTherm III T8601C (with wires R, G, B, W, Y ) . White wire is connected to O terminal , Yellow wire is connected to W terminal. Also W and Y and connected using jumpers. I want to replace this with Nest. Need help with wiring.
Update: I have Heat pump model CPE30-1AB Goodman heat pump. Very Old Model but runs gr8...running for 30th year.
Nest terminals are as shown in pic
06-11-2023 07:42 PM
I was not able to start conversation as reply button was disabled. So I am Updating my original post by replying to my post: I have Heat pump model CPE30-1AB Goodman heat pump. Very Old Model but runs gr8...running for 30th year.
Nest terminals are as shown in pic
06-12-2023 03:12 PM
See your other post for an answer.
06-15-2023 12:16 PM
Hi everyone,
Your thread is now identical to this primary post. The main thread will be where you'll find all the updates on this matter, so we advise checking and updating it as needed.
Best,
Mark
06-15-2023 12:54 PM
thanks @Markjosephp