08-02-2022 10:42 AM
The fan stopped working after a power outage. Fan is not running at all. The A/C unit is less than 6 years old.
08-02-2022 11:45 AM
Hello Juan,
Let us do some checking.
1. When you turn in the AC in cooling mode, does the blower fan come on?
2. When you put the system in Heating Mode does the blower fan come on?
3. when you put it in Cooling mode and go outside, is the outdoor unit running?
Sometimes. Power outage and the inrush of power when restored by the power company causes a low voltage the fan capacitor can get damaged. Please report back your findings.
08-02-2022 12:23 PM
08-02-2022 12:28 PM
This sounds like the capacitor on the blower has failed. You will need and HVAC technician to come check it out.
08-02-2022 12:55 PM
Thank you Cooling Wizard
08-02-2022 03:15 PM
Online, Look up AC Cooling Wizard, in El Centro, CA and give a call, please.
08-05-2022 05:28 PM
Hi folks,
@CoolingWizard, thanks for the help!
@Juan4, how's it going with your Nest Thermostat? Still need our help?
Thanks,
Edward
08-06-2022 08:32 AM
Hi Edward,
The board of the motor burned out in the last blackout. I needed to replace the motor. Thank you for your collaboration. Case closed - Damaged fan motor.
08-08-2022 06:24 PM
Hey Juan4,
Got it and you're welcome! We're glad to hear that you've found the cause of your concern so you know how to resolve it. We'll go ahead then and lock this thread after a day. If you have any new issues, updates or just a discussion topic, feel free to start a new thread in the Community.