i have 5 wires coming from wall R,Y,G,W1,W2 . The nest thermostat i have does not have W2 but has O/B. So when i made a simulated run using Google home it showed i connect W2 to W2 but there is no W2 on nest
08-09-2023 01:01 AM
Try leaving W2 disconnected tape off or cut off strip later. Should work on 1 stage of heat. W1 W2 are for single and dual stage heating.
08-14-2023 04:52 PM
Hi there,
Thanks for reaching out. I'm sorry for the delay. The *OB terminal in the Nest Thermostat E is for either emergency heat/auxiliary heat, heat pump, and stage 2 heating or cooling. As long as your system is working as it should, you don't have anything to worry about.
I appreciate the input, @HVAC.
Best,
Jenelyn