Wiring photo to check compatibility

ISG
Community Member

Posting photo to check compatibility 

IMG_4777.jpeg

73 REPLIES 73

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@ISG , you thermostat is set up for a Heat Pump with auxiliary heat and emergency heat. You will need a Nest Learning Thermostat and Your wires in use are

R, W2/X, W1, Y, G, O, B

R - Red Wire, 24VAC Power Input, place on Nest R or Rc

W2/X Black Wire, Emergency Heat, place on Nest *

W1 White Wire, Auxiliary Heat, place on Nest W2/AUX

Y Yellow Wire, Compressor Relay, place on Nest Y1

G Green Wire, Blower Fan Relay, place on Nest G

O Orange Wire, Change Over Valve, place on Nest OB

B Blue Wire, 24 VAC Power Common


AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

Wow this is great. Thank you so much!

BrianH
Community Member

How do I upload a photo to check compatibility? 

Cooling wizard thank you again I got it wired and system is working. Can you look at my setup page and see if it looks right to you. Also sending pics of my heat pump. 

IMG_4782.png

IMG_4780.jpeg

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@ISG, you have a heat pump, which is electrical, and your indoor air handler is your forced air and must have an LP burner type furnace connected to your air handler.  In this case you have set the Auxiliary heat to never be used. I am just checking, do you have a LP gas furnace?

 

AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

Thank you CW. This is a new house I just bought in the NC mountains. When I’m back up there this weekend I will check. Any advice on how I can tell if I have a gas furnace or not? Sorry for being so naive. 

Jenelyn_O
Community Specialist
Community Specialist

Hi everyone, 

 

Thanks for reaching out. I'm sorry for the delay. I'd love to help. 

 

We're sad to see you go, BrianH. We hope we can make it up to you in the future. Send us a message if you change your mind. 

 

@ISG, if you have a gas furnace there would be a small window on the front of the furnace where you should see a blue glowing flame. Also, you might smell like a little bit of gas when your heating is running. 

 

I appreciate the help, @CoolingWizard and @ayazghusain1.

 

Best,

Jenelyn

zoeuvre
Community Specialist
Community Specialist

Hi ISG, 

 

I want to check and see if you are still in need of any help. Please let me know, as I would be happy to assist and answer any questions you may have.
 

Thanks,

Zoe

ISG
Community Member

Thank you Zoe. So I just got back to the house and there is no sign of a pilot light so I think I must have an electric furnace. 

I guess I should change my settings right?

Actual unit

IMG_4784.jpeg

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@ISG , I am sorry it took so long for me to reply. I hate that other users do not create their own thread for help and then clutter yours message thread. I just found your picture of the furnace.  Your furnace is an electric furnace.  Unfortunately, the installer did not mark which if any electric heat kit was installed.  It should have been marked in Column A of the label. I do not know much about North Carolina and the specific area your state your home is in.  Your old thermostat is wired with W1 and X. This is an indication there is Auxiliary heat and and emergency heat. As for your Nest Equipment setup, you do not have a “duel fuel” system, you have a single fuel system and that is Electric.  So I am going to walk you through how to change this. 

At your thermostat, wake up the display, select SETTINGS, once in settings go to EQUIPMENT and select it. You need to choose CONTINUE, and CONTINUE.  Now we are going to go into PRO SETUP. 
Once you select PRO SETUP, you will get a warning, select CONTINUE. Now you will see a representation of the nest backplate and wire attached.  Rotate the ring and select the W2 wedge and select it.  Now select the Heat Type and change it from LP to Electric. Rotate and select DONE.  When asked, you have a Single Fuel system. 

Reach out to me if you need any additional help

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

  • Hi could you check if my unit is comparable it has the same color is wire but different place

Just want to make sure I have it  first time DIY IMG_6086.jpgIMG_6087.jpgIMG_6088.jpg

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@BrianH , aWhen you are logged in, and you open a test box to reply, you will see a camera icon at the top of the text box.  Tap that camera and pick your pictures.  

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

There is no option to upload a photo. Is there an email address I can send the pick to? 

No option to add a photo  when replying to a current message. 

FYI, the help page link goes directly to this thread, rather to a parent in the forum. It is unclear how to start a new thread, especially to those new here. Disparaging them is not useful. 

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@CourteVV , it is very simple to start a conversation. At the the top of the forum, in this case, Thermostats, you see the START CONVERSATION button.  It is that simple. And I am not disparaging any individual by name. When  multiple people start posting their problem inside another persons thread, it clutters the thread up and makes it difficult to follow original thread and support the original poster. 

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

CoolingWizard
Platinum Product Expert
Platinum Product Expert

Make sure your email you used to access this community is confirmed and approved.  Here is am image of the camera.

IMG_1934.jpeg

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

20230703_125936.jpg

 my system is a heat pump for AC and cooling with emergency heating.  Is this compatible woth Google nest.  Also , I wonder if I don't need the learning version as with a heat pump you don't want the temptation vary that much. 

@CourteVV , the dark blue wire is your power Common and X wire is your Emergency heat and the W1 is your Auxiliary heat. 

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

BrianH
Community Member

20230703_125936.jpg

 I have a heat pump for AC and heating. Not connected to the HVAC.  Will Google Nest work with this configuration? 

CoolingWizard
Platinum Product Expert
Platinum Product Expert

Yes indeed your system is compatible with the Nest Thermostat.  Your wires in use are:

R; red wire, 24VAC power

Y1; yellow wire, Compressor Relay - Heat and Cool

E; brown wire, Emergency Heat

W2; white wire, Auxiliary Heat

O; Orange Wire, Reversing Valve relay

You have a blue wire not assigned. You should consider using this wire for the 24VAC Power Common. This will require you going to the Air Handler and make sure the blue wire is connected to the C terminal their. As well.  

 

AC Cooling Wizard

 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

I have a left over wire  - Brown 'E' and no where to put it. The Google Nest only has 6 wiring slots.

What turned on - I get a Error code : E294 - no R - yet it is definitely connected.

 

Any ideas?

 

Thank you ,

 

Brian

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@BrianH , on that thermostat you have, the single * is the only programable function connection.  It can only be programmed for a single function. And your Nest Model does not support your system configuration. You need a Nest Learning Thermostat in order to support heat pump with auxiliary heating And Emergency heating.

AC Cooling Wizard 

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

If the E and W2 wire go to the same place on the Air Handler, the Nest Thermostat can activate the Aux strips on its own when you select "emergency heat" in the app. This allows you to discard the E wire and use the Nest Thermostat and not the learning stat. 

It hot here - thus am giving up. I called my heating guy, returning the nest and having an Ecobee installed tomorrow AM.

MrsSommerfeld
Community Member

image.jpg

We had a American Standard thermostat on same brand of gas furnace. Wires don’t have colour coding and were labeled D-Data, R-24vac hot, and B-24vac common. There was also a fourth, white wire not mentioned in the manual and not connected to the previous thermostat. We have no idea how to wire our Nest into this. Help!

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@MrsSommerfeld , your question is unique to and should be in its own message and not added to @ISG‘s original message thread.  

 Now then your American Standard system is using a digital communications interface and not the normal conventional HVAC control system. Most systems that have a digital communication interface also have conventional terminals as well.  You will be required to install a new 7 to 10 conductor thermostat cable between your thermostat and the air handler.  

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

Hi folks,

 

@ISG, I just want to check if you were already able to change your thermostat settings. How's your Nest Thermostat now? 

 

@MrsSommerfeld, I hope you got the answer you're looking for. Please let us know if you still have questions in mind, as we'll be willing to assist you. 

 

I appreciate the help, @CoolingWizard.

 

Kind regards,

Jenelyn

Mokonski
Community Member

IMG_1101.jpeg

 I’m getting mixed messages whether Nest is compatible or not: connected wires are R, W, Y, G, O, B with a jumper between W2/X2 and W.

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@Mokonski , on your old thermostat, I cannot quite see the letters behind the white wire and the jumper.  It looks like W2 and X.  
You Blue wire in B is your Power Common.

The Orange  wire in O is your heat pump reversing valve. This changes the heat pump mode.
The Green wire in G is the Blower Fan Relay, this turns the blower fan on. 
The Yellow wire in Y controls the Compressor relay.  
The White wire in W is auxiliary heat. This is typically electric heat strips located in the air handler. 
The jumper wire to W2/X is for emergency heat. 
The Red wire in R is the 24VAC Power In.

The Blue wire connected to B is the Power Common.  

Your system is fully compatible with the Nest Learning Thermostat 3rd Generation. 

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

Great reply, thank you! 

Have to ask, is this compatible with Nest thermostat (i.e. not the Learning thermostat)? I'm reading that there are some differences.

zoeuvre
Community Specialist
Community Specialist

Hi folks,

 

@Mokonski, chiming in — based on the information given by CoolingWizard, your thermostat wires should be wired to our Nest Learning Thermostat 3rd generation. You can use this guide in installing and setting up your Nest Learning Thermostat. 

 

@MrsSommerfeld, I want to check and see if you are still in need of any help. Please let me know, as I would be happy to assist and answer any questions you may have.

 

I appreciate your help here, @CoolingWizard and Jenelyn. 

 

Best,

Zoe

Markjosephp
Community Specialist
Community Specialist

Hello there,

 

I'm checking back in — how's it going? Still need our help?
 

Thanks for your assistance here, Zoe.

 

Regards,
Mark

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@Mokonski , i’m sorry for the delay in responding. Unfortunately because you have the auxiliary and emergency heat and the heat pump, etc. so you will actually require a nest learning thermostat.

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.

Hello everyone,

 

I don't want to be a nudge, but I'd like to check if you were able to get the answer you were looking for about compatibility. Feel free to reach out again if you still need help.

 

I appreciate your continued help, @CoolingWizard.

 

Thanks,

Mark

natasha3704
Community Member

IMG_0897.jpeg

I am installing the 3rd Gen Nest Learning Thermostat. I’m unsure of what to do with the W/E wire. Is it compatible?

CoolingWizard
Platinum Product Expert
Platinum Product Expert

@natasha3704 , your system is a conventional HVAC system.  The W/E wire is your primary heat. This wire will end up on W1.  Your wires in use are: Rc, W, G, Y.

AC Cooling Wizard

NestPro, Google Pro, Mechanical Engineer and HVAC service company owner.